CI854-CI860 Problem
Hello,
Im working with System 800xA v.5.1 Rev B
In my project (Control Builder M) Im working with a PM866.
Position 1: CI854
Position 2: CI860
I downloaded the firmware for the controller and the CI´s (CI854 and CI860).
The thing is that when doing a Download I have the following Warnings:
-Firmware for unit CI854 at position 1 is not compatible with connected library
-Firmware for unit CI854 at position 1 is not compatible with connected library
When im online I have errors in the CI´s
-Wrong device type.
I changed the connected libraries for others versions and didnt worked.
The problem disappears when I do a download with CI854 alone, or CI860 alone.
Someone knows what is happening?
Thanks!
Answers
Hello
Try upgrade firmware from the Control Builder AC 800M Rev.C.
The firmware files are usually located in the "\Engineering & Development\Control Builder M\FirmwareFiles\bin" of 800xA installation media.
Hello,
Can you provide the information, when you access remote system and check the firmware what is showing and in the library from the drop downlist what is available.
Which version is higher?
If you download it will work fine, the behavior of download firmware is like this
X version < Y version trying to upgrade to Y but fails so it needs to be at X version itself, this version will be activ once you download the configuration.