Freelance 9.2 Hart Connection
Hello
I am about to finish my project with Freelance v9.2
In Field ı have devices with HART, and in my system ı have AI815(HART supported)
How can ı connect to these HART devices from SCADA PC
It is not necessary to integrate it to Digivis, I just need to reach it from my PC
Thanks.
Voted best answer
Hi,
You need FDT/DTM for that(it needs professional license),
There are two ways you can reach to device via DTM,
1) from CBF, install that particular device DTM on cbf PC (check compatibility)
Then instantiate that device dtm beneath AI815 channel.
Save the configuration > run plausibility check > goto commissioning mode
Right click on device dtm node and you can download or upload from device.
This way you can go online with your hart device.
2) once commissioned as above download changes to digiVis
Now enter into diagnostic mode in system display (in system display > goto operate menu item > enter diagnostic mode > password is 'admin'
Now click on DTM in hw tree and call device dtm and you can view device dtm.
Pls check associated app,
and for compatibility check this link http://www05.abb.com/global/scot/scot313.nsf/veritydisplay/90b6646a97808b1ac125
7d650008a982/$file/3BDD011926_AK_en_Freelance_Integrated_HART_Devices.pdf
Hope that helps
Add new comment