S800 IO Module Hardware Missing in 800xA for Advant
Hi, Everyone.
This is related to 800xA for Advant.
I have a problem for S800 IO Module Hardware Missing like pictures.
but, AF100 Status and Cluster Status are good like pictures.
also, IO Channel of HW Missing Module have good signal.
I get suspicious about having Only S800 IO Module HW Missing Error.
refer to pictures.
Wait your answer.
Thanks.
Answers
As for the pictures I can only assume the following.
The AF100 is showing the communication interface status of controller which is ok.
The Cluster picture shows you the status of the cluster modem which is ok.
The module picture is definetly not ok. Have you checked the module physically by sight? Any diagnostics on the LED of the module? AI810 are also Hot swappable module, perhaps if there is no risk for your process you should try to swap the module and see what happens with the diagnostics.
It is not enough just by seeing the printscreens to give a adequate solutiuon.
I had checked the module physically by sight and it's okay. also, all signals of modules having HW Missing is good.
The diagnostics on the LED of the modules is nothing and it's just R(un) LED.
Do you need the evidence to solve this problem??
wait for your other answer.
thanks for your answer.
Source:
If you have AF100 physical link made by truck cable and TC505/TC506 terminal units and you have wrong type of cable or cable shield is grounded both end, you can have that kind of diagnostics. Use correct cable (IBM Type ..something) and check shielding.
tto
by tomo Rank: 2130 on 12/9/2015 10:02:23 AM | Like (0) | Report
Hi, have you solved your problem? I have the exact same thing. Everything seems to be fine just wrong Module status. When I check subscribe for live data in control connection i get BadQuality.