Deploy going in idle ( plant explorer workplace 800XA 5.0)
Hi
I was asking, in plant explorer workplace after modifying r adding any object in control structure at the time of deploy it showing rollback error and system going in idle. if i restart server i may get back but frequently it happening.
How could i over come with this problem? suggest me.....
Answers
AT FIRST TAKE A COMPLETE BACKUP.
Now, It usually happens, when you have deleted one of your Signal/Aspect of your Object in Control Structure in wrong way(which you have created in Object Structure).
Check which service is unhealthy at that time.(it will let you know the exact cause).
If you can diagnose,on which object you have done such R & D. Then best soluton is then delete that object, and then recreate a new one similar to that. And then use it further where you need nto.
Still if problem persists,then you can Create a New Controller Type,and then configure it in control Structure, and then check all your services are healthy .
by SG Rank: 35 on 1/29/2015 8:22:44 PM | Like (0) | Report
A Screenshot of error/errorcode will be more helpful..
by IEFIOSU Rank: 728 on 1/30/2015 3:45:35 AM | Like (0) | Report
What do you mean by deploy, what are you trying to do?
by SG Rank: 35 on 2/8/2015 8:54:02 PM | Like (0) | Report
In Case of PLC Connect, the Engineering part is slightly lengthier..Mirroring will not be there between Control builder & PPA..So whenever you call an opc tag from control builder to plant explorer workplace, deploy has to be done..In short, Just like download for Controlbuilder, Deploy is for Plant explorer workplace when PLC connect is used..
Add new comment