Hello,
I need to communicate an AC800F with an RTU through ModBus TCP but I'm not sure if that's possible with the actual system. I have an AC800F with an EI 803F module connected to a switch where the RTU is also connected. Can you please help me? Is it possible to configure the AC800F to transmit using ModBus?
Thanks in advance for your help.
Voted best answer
Answers
buy one TCP / RTU convertor, this is the easiest way to complete your job.
Hi,
Please note in Freelance 2013 SP1 AC 800F supports Modbus TCP, So in that version it's straight forward communicate with rtu over modbus tcp. if you have version lower than F2013 SP1 then as suggested in second answer use converter rtu/tcp. note that in AC 800F you need card CI820F and TB 870 with cable TK821.