PM861 processor going into fault mode repeatedly
Answers

by akbokade Rank: 684 on 1/27/2015 7:38:18 AM | Like (0) | Report
Sorry i cannot share with you the CPU logs. Can you suggest me possible reasons for this behaviour of the processor
by Rob Lyon

I worked on a controller once where rats had made a nest on top of the CPU and urinated all over the boards. That controller used to fault often.
Idle speculation about possible causes when there is no diagnostic information available doesn't really help anyone.
by akbokade Rank: 684 on 2/9/2015 6:05:44 AM | Like (0) | Report
I have the CPU logs .. can someone give their mail id so that i can mail the log files.
by akbokade Rank: 684 on 2/10/2015 1:52:53 AM | Like (0) | Report
##########################
=== Latest startup-log ===
##########################
_____________________________________________________________________________
bad/missing battery - Controller Reset will follow!
0
No Firmware Upgraded
5.5.2 2096
Watchdog is enabled with timeout = 1962 us
This is Lower CPU running as Primary CPU (previously Undefined CPU).
DDCC+ test: Test OK
ching interface lo0...done
TCPIP CONFIG
I 1979-12-31 00:00:00.000 Printer thread MMS-plugin, streaming disabled
I 1979-12-31 00:00:00.000 Printer thread, Filter: Disabled, Mode: Classic, BUM: Disabled
I 1979-12-31 00:00:00.000 Low memory (0x00-0x3F) access detection initiated
I 1979-12-31 00:00:00.000 Built: Apr 16 2011 20:45:48
I 1979-12-31 00:00:00.000 Autorestart is disabled
I 1979-12-31 00:00:00.000 Initialized. No time data available.
I 1979-12-31 00:00:00.002 System time quality: BAD
I 1979-12-31 00:00:00.004 CPU-core running at 48 Mc, to=16.0 us
I 1979-12-31 00:00:00.541
I 1979-12-31 00:00:00.555 Network Interface 10.120.100.13 (255.255.255.0 ) : 00-00-23-13-ab-72
I 1979-12-31 00:00:00.565 Network Interface 10.121.100.13 (255.255.255.0 ) : 00-00-23-13-ab-73
I 1979-12-31 00:00:00.572 Backup Interface 10.120.102.13 (255.255.255.0 ) (default rule)
I 1979-12-31 00:00:00.575 Backup Interface 10.121.102.13 (255.255.255.0 ) (default rule)
I 1979-12-31 00:00:00.576 Toolport IP adress 192.168.255.254 (255.255.255.0 )
I 1979-12-31 00:00:00.579 Thread switch log was initiated for 100 entries
I 1979-12-31 00:00:00.579 Thread switch logging is ON
I 1979-12-31 00:00:00.595
I 1979-12-31 00:00:00.596
I 1979-12-31 00:00:00.598 Product : AC 800M PM861
I 1979-12-31 00:00:00.599 Version : 5.1.0/1 (Build 5.1.100.13)
I 1979-12-31 00:00:00.600 Created : 2011-04-17
I 1979-12-31 00:00:00.601 ABB AB
I 1979-12-31 00:00:00.602
I 1979-12-31 00:00:00.603 Controller Reset
I 1979-12-31 00:00:00.801 Position Module Firmware Name Date Version
I 1979-12-31 00:00:00.802 0(L) PM861 FW861 2011-04-17 5.1.100.13
I 1979-12-31 00:00:00.803 OMEGA 2011-04-16 5.1.100.13
I 1979-12-31 00:00:00.804 CPU Unit N/A PM861A E
I 1979-12-31 00:00:00.804 Backplane N/A TP830 C
I 1979-12-31 00:00:00.805 FPGA N/A 1.3/0
I 1979-12-31 00:00:00.806 CEX Master N/A 2.3
I 1979-12-31 00:00:00.807 CEX Slave N/A 1.1
I 1979-12-31 00:00:00.808 CPU Chip N/A 0502
I 1979-12-31 00:00:00.808 RCU N/A 2.1
I 1979-12-31 00:00:00.810 1 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 1979-12-31 00:00:00.811 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 1979-12-31 00:00:00.812 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 1979-12-31 00:00:00.813 CI-Unit N/A CI854A PR:J
I 1979-12-31 00:00:00.814 2 Unknown
I 1979-12-31 00:00:00.815 3 Unknown
I 1979-12-31 00:00:00.816 4 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 1979-12-31 00:00:00.817 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 1979-12-31 00:00:00.818 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 1979-12-31 00:00:00.819 CI-Unit N/A CI854A PR:J
I 1979-12-31 00:00:00.821
I 1979-12-31 00:00:00.822 Actual heapsize: 9052 kBytes
I 1979-12-31 00:00:00.909 Network address is 10.120.100.13, 10.121.100.13.
I 1979-12-31 00:00:01.447 RunMode
I 1979-12-31 00:00:01.597 License Manager: Feature Name Control_Software
I 1979-12-31 00:00:01.598 License Manager: Version 5.1.0
I 1979-12-31 00:00:01.599 License Manager: Hardware ID 00-00-23-13-ab-72
I 1979-12-31 00:00:01.697 System Initialized.
I 1979-12-31 00:00:01.698 Redirection of Console Channel to System log file I 1979-12-31 00:00:04.140
I 1979-12-31 00:00:04.141
I 1979-12-31 00:00:04.152 Network Interface 192.168.255.254(255.255.255.0 )
ppp4: ppp 2.1.2 started by
ppp4: Connect: ppp4 <--> /tyCo/0
I 1979-12-31 00:00:06.643 4005 P:Backup CPU started
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.5 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 1979-12-31 00:00:09.980 NSP, Network Storm Protection started,limit = 800 pkt/s
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 1979-12-31 00:00:11.613 Hot insert on CEX module number 2 is being performed
I 1979-12-31 00:00:11.615 Hot insert on CEX module number 3 is being performed
I 1979-12-31 00:00:11.892 Position Module Firmware Name Date Version
I 1979-12-31 00:00:11.894 2 CI867 VICIdrv 2010-02-18 7.12
I 1979-12-31 00:00:11.895 FWCI867 2011-04-12 5.1.0111.0
I 1979-12-31 00:00:11.896 FPGA(15) N/A 0.1/0 B0
I 1979-12-31 00:00:11.897 HW revision N/A CI867 C
I 1979-12-31 00:00:11.898 CPU Chip N/A 0700
I 1979-12-31 00:00:11.899 Cirrus 2009-01-16 5.1.0000.0
I 1979-12-31 00:00:11.904 CEM Revcode N/A Unknown (0x00)
I 1979-12-31 00:00:12.182 Position Module Firmware Name Date Version
I 1979-12-31 00:00:12.184 3 CI867 VICIdrv 2010-02-18 7.12
I 1979-12-31 00:00:12.185 FWCI867 2011-04-12 5.1.0111.0
I 1979-12-31 00:00:12.186 FPGA(15) N/A 0.1/0 B0
I 1979-12-31 00:00:12.187 HW revision N/A CI867 C
I 1979-12-31 00:00:12.188 CPU Chip N/A 0700
I 1979-12-31 00:00:12.189 Cirrus 2009-01-16 5.1.0000.0
I 1979-12-31 00:00:12.194 CEM Revcode N/A Unknown (0x00)
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
##############################################
=== Log fetched at 2015-02-09 18:05:17.965 ===
##############################################
_____________________________________________________________________________
bad/missing battery - Controller Reset will follow!
0
No Firmware Upgraded
5.5.2 2096
Watchdog is enabled with timeout = 1962 us
This is Lower CPU running as Primary CPU (previously Undefined CPU).
DDCC+ test: Test OK
ching interface lo0...done
TCPIP CONFIG
I 1979-12-31 00:00:00.000 Printer thread MMS-plugin, streaming disabled
I 1979-12-31 00:00:00.000 Printer thread, Filter: Disabled, Mode: Classic, BUM: Disabled
I 1979-12-31 00:00:00.000 Low memory (0x00-0x3F) access detection initiated
I 1979-12-31 00:00:00.000 Built: Apr 16 2011 20:45:48
I 1979-12-31 00:00:00.000 Autorestart is disabled
I 1979-12-31 00:00:00.000 Initialized. No time data available.
I 1979-12-31 00:00:00.002 System time quality: BAD
I 1979-12-31 00:00:00.004 CPU-core running at 48 Mc, to=16.0 us
I 1979-12-31 00:00:00.541
I 1979-12-31 00:00:00.555 Network Interface 10.120.100.13 (255.255.255.0 ) : 00-00-23-13-ab-72
I 1979-12-31 00:00:00.565 Network Interface 10.121.100.13 (255.255.255.0 ) : 00-00-23-13-ab-73
I 1979-12-31 00:00:00.572 Backup Interface 10.120.102.13 (255.255.255.0 ) (default rule)
I 1979-12-31 00:00:00.575 Backup Interface 10.121.102.13 (255.255.255.0 ) (default rule)
I 1979-12-31 00:00:00.576 Toolport IP adress 192.168.255.254 (255.255.255.0 )
I 1979-12-31 00:00:00.579 Thread switch log was initiated for 100 entries
I 1979-12-31 00:00:00.579 Thread switch logging is ON
I 1979-12-31 00:00:00.595
I 1979-12-31 00:00:00.596
I 1979-12-31 00:00:00.598 Product : AC 800M PM861
I 1979-12-31 00:00:00.599 Version : 5.1.0/1 (Build 5.1.100.13)
I 1979-12-31 00:00:00.600 Created : 2011-04-17
I 1979-12-31 00:00:00.601 ABB AB
I 1979-12-31 00:00:00.602
I 1979-12-31 00:00:00.603 Controller Reset
I 1979-12-31 00:00:00.801 Position Module Firmware Name Date Version
I 1979-12-31 00:00:00.802 0(L) PM861 FW861 2011-04-17 5.1.100.13
I 1979-12-31 00:00:00.803 OMEGA 2011-04-16 5.1.100.13
I 1979-12-31 00:00:00.804 CPU Unit N/A PM861A E
I 1979-12-31 00:00:00.804 Backplane N/A TP830 C
I 1979-12-31 00:00:00.805 FPGA N/A 1.3/0
I 1979-12-31 00:00:00.806 CEX Master N/A 2.3
I 1979-12-31 00:00:00.807 CEX Slave N/A 1.1
I 1979-12-31 00:00:00.808 CPU Chip N/A 0502
I 1979-12-31 00:00:00.808 RCU N/A 2.1
I 1979-12-31 00:00:00.810 1 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 1979-12-31 00:00:00.811 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 1979-12-31 00:00:00.812 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 1979-12-31 00:00:00.813 CI-Unit N/A CI854A PR:J
I 1979-12-31 00:00:00.814 2 Unknown
I 1979-12-31 00:00:00.815 3 Unknown
I 1979-12-31 00:00:00.816 4 CI854 CI854 OMEGA driver 2004-09-14 02.03
I 1979-12-31 00:00:00.817 FWCI854 PROG 3611540 A 2009-12-01 05.59
I 1979-12-31 00:00:00.818 FWCI854 BOOT 3611539 D 2003-10-20 03.04
I 1979-12-31 00:00:00.819 CI-Unit N/A CI854A PR:J
I 1979-12-31 00:00:00.821
I 1979-12-31 00:00:00.822 Actual heapsize: 9052 kBytes
I 1979-12-31 00:00:00.909 Network address is 10.120.100.13, 10.121.100.13.
I 1979-12-31 00:00:01.447 RunMode
I 1979-12-31 00:00:01.597 License Manager: Feature Name Control_Software
I 1979-12-31 00:00:01.598 License Manager: Version 5.1.0
I 1979-12-31 00:00:01.599 License Manager: Hardware ID 00-00-23-13-ab-72
I 1979-12-31 00:00:01.697 System Initialized.
I 1979-12-31 00:00:01.698 Redirection of Console Channel to System log file I 1979-12-31 00:00:04.140
I 1979-12-31 00:00:04.141
I 1979-12-31 00:00:04.152 Network Interface 192.168.255.254(255.255.255.0 )
ppp4: ppp 2.1.2 started by
ppp4: Connect: ppp4 <--> /tyCo/0
I 1979-12-31 00:00:06.643 4005 P:Backup CPU started
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.13 is on lo0 but got reply from 00:00:23:13:ab:72 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.5 is on cpm0 but got reply from 00:00:23:18:3f:1a on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 1979-12-31 00:00:09.980 NSP, Network Storm Protection started,limit = 800 pkt/s
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 1979-12-31 00:00:11.613 Hot insert on CEX module number 2 is being performed
I 1979-12-31 00:00:11.615 Hot insert on CEX module number 3 is being performed
I 1979-12-31 00:00:11.892 Position Module Firmware Name Date Version
I 1979-12-31 00:00:11.894 2 CI867 VICIdrv 2010-02-18 7.12
I 1979-12-31 00:00:11.895 FWCI867 2011-04-12 5.1.0111.0
I 1979-12-31 00:00:11.896 FPGA(15) N/A 0.1/0 B0
I 1979-12-31 00:00:11.897 HW revision N/A CI867 C
I 1979-12-31 00:00:11.898 CPU Chip N/A 0700
I 1979-12-31 00:00:11.899 Cirrus 2009-01-16 5.1.0000.0
I 1979-12-31 00:00:11.904 CEM Revcode N/A Unknown (0x00)
I 1979-12-31 00:00:12.182 Position Module Firmware Name Date Version
I 1979-12-31 00:00:12.184 3 CI867 VICIdrv 2010-02-18 7.12
I 1979-12-31 00:00:12.185 FWCI867 2011-04-12 5.1.0111.0
I 1979-12-31 00:00:12.186 FPGA(15) N/A 0.1/0 B0
I 1979-12-31 00:00:12.187 HW revision N/A CI867 C
I 1979-12-31 00:00:12.188 CPU Chip N/A 0700
I 1979-12-31 00:00:12.189 Cirrus 2009-01-16 5.1.0000.0
I 1979-12-31 00:00:12.194 CEM Revcode N/A Unknown (0x00)
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
I 1979-12-31 00:00:14.676 Init Log Saved
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 1979-12-31 00:00:29.334 Create applications definition domain
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 2015-02-09 18:03:44.980 New time zone: India Standard Time
I 2015-02-09 18:03:45.047 Create controller configuration domain
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 2015-02-09 18:03:47.788 AE System events to controller log: Medium Severity
I 2015-02-09 18:03:47.805 4006 P:Primary CPU Synchronized state
I 2015-02-09 18:03:47.891 Protocol Handler Name = PhIPpin
I 2015-02-09 18:03:47.891 Version = 5.1.6.0 ; 2009-10-23
I 2015-02-09 18:03:47.892 Ph binary version = : 0x00001264
I 2015-02-09 18:03:47.897 Protocol Handler Name = PhIAC_MMS
I 2015-02-09 18:03:47.898 Version = 5.1.8.6 ; 2010-05-27
I 2015-02-09 18:03:47.899 Ph binary version = : 0x0000870E
I 2015-02-09 18:03:47.910 Protocol Handler Name = PHModulebus
I 2015-02-09 18:03:47.911 Version = 5.1.46.301; 2010-03-17
I 2015-02-09 18:03:47.912 Ph binary version = : 0x00000000
I 2015-02-09 18:03:47.929 Protocol Handler Name = PHCI854
I 2015-02-09 18:03:47.930 Version = 05.01-04 2011-02-23
I 2015-02-09 18:03:47.931 Ph binary version = : 0x00003D5F
I 2015-02-09 18:03:47.933 453 PhCI854 0 0 0 /root/PhProfibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2015-02-09 18:03:47.935 454 Ph Versions: 5 1 4 /root/PhProfibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2015-02-09 18:03:47.937 455 Ph Date: 7DB 2 17 /root/PhProfibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2015-02-09 18:03:47.948 Protocol Handler Name = PhMODBUSTCP
I 2015-02-09 18:03:47.949 Version = 5.1.0111.00 ; 12-APRIL-2011
I 2015-02-09 18:03:47.950 Ph binary version = : 0x00006834
I 2015-02-09 18:03:48.022 PhIAC_MMS @ 0.5.1 Configure received 13 ULONG(s). ArraySize: 5
I 2015-02-09 18:03:48.030 CPhIAC_MMS::DoWork starting up
I 2015-02-09 18:03:48.231 Webserver ready for login
I 2015-02-09 18:03:48.260 6352 config: PhResp. running... 1 0 0 /root/PhProfibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2015-02-09 18:03:48.263 6516 Created 1st driver 1 1 938884 /root/PhProfibus/PH/ProtocolHandler/Source/PhCI854/PhCI854.cpp
I 2015-02-09 18:03:48.290 1942 CPhCI854Base::Configure 4 0 0 CI854ConfigBase.cpp
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 2015-02-09 18:03:49.029 2652 General: Config succeeded 4 0 0 CI854ConfigBase.cpp
I 2015-02-09 18:03:49.030 1942 CPhCI854Base::Configure 1 0 0 CI854ConfigBase.cpp
E 2015-02-09 18:03:49.359 On Unit= 1.2 HWError PLC_1 0000 See HWTree Error 16#00010001 16#40000001
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
E 2015-02-09 18:03:49.361 On Unit= 1.2.1 HWError PLC_1 0000 See HWTree Error 16#00000001 16#00000000
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
E 2015-02-09 18:03:49.362 On Unit= 1.2.2 HWError PLC_1 0000 See HWTree Error 16#00000001 16#00000000
I 2015-02-09 18:03:49.936 2652 General: Config succeeded 1 0 0 CI854ConfigBase.cpp
I 2015-02-09 18:03:50.216 New I/O-connections configuration.
I 2015-02-09 18:03:50.480 I/O-connections configuration waiting for application/s.
I 2015-02-09 18:03:50.587 Create application instance domain: R559493129Application_1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 2015-02-09 18:03:51.391 Create application R559493129Application_1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
I 2015-02-09 18:03:52.075 IAC: Connection up (IP = A786406)
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
I 2015-02-09 18:03:52.186 I/O-connections configured.
I 2015-02-09 18:03:52.297 Start application R559493129Application_1
E 2015-02-09 18:03:52.614 NetInterSup No route to host
E 2015-02-09 18:03:52.614 NetInterSup Failed to send message to backup CPU
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
W 2015-02-09 18:03:54.765 A/E Burst: Prevented 61 alarms & events from being printed in the log, refer to an OPC AE client for more info.
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.12 is on cpm0 but got reply from 00:00:23:13:9c:34 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.22 is on cpm0 but got reply from 9c:8e:99:4f:5e:88 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.113 is on cpm0 but got reply from 88:51:fb:42:d4:f1 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.114 is on cpm0 but got reply from d4:c9:ef:f4:0c:14 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.21 is on cpm0 but got reply from 9c:8e:99:4f:6d:16 on cpm1
0x85e798 (tNetTask):
arp: 10.120.100.40 is on cpm0 but got reply from 10:60:4b:7d:da:ce on cpm1
by akbokade Rank: 684 on 2/10/2015 1:55:26 AM | Like (0) | Report
Above is the CPU log
by Rob Lyon

It looks like there is no crash log because you have no battery either in the controller or in the SB821. What you see is only the startup log.
Also, you are getting some error messages indicating that some IP adresses (10.120.100.21 and 10.120.100.21 ) are responding on the wrong Network port. You may have a cross connection in a network somewhere. Also, there is at least one message indicating that network storm protection is activated. arp is address routing protocol. Google arp for information on how IP adresses are resolved to MAC addresses and try to sort out which network card is tied to which IP address.
by Rob Lyon

*10.120.100.40
* also, install or replace the backup battery.
Add new comment
Hello,
At first, make sure that you are doing no mistake from the standard way of doing the configuration.
And now at last, We are into the same issue.
Thus without wasting time, be in touch with local ABB team.
Source:
Add new comment