Hi,
We are have tried to restrore backup from 800xa 4.1 system to 800xa 5.1 , But th all VB displays are comming up with Error .
Activex.X HRESULT = 0X800a0153 .
After Restoration the we have done the follwowing :
We have installed 800M Connect VB Graphics Extensions.
Visula Basic SP6 is installed.
Any one can give the steps for uprade , after this we would like to use VB migration tool to convert displays to PG2
Regards
Answers
Please deploy each VB graphics after restoration.
Hello,
Always all graphics should be deployed since in VB there are saved graphics are really not updated in operator graphics so it needs deployment so before taking backup ensure all graphics are deployed you can do it in one shot through deploy tool.
After that take the full backup & restore in machine(it should have the same system softwares should be loaded & VB graphics extensions to be loaded as part).
Load the license & then you check it should work.
From your comments to Harsha D.
If elements are disappearing from your graphics ( and getting replaced by purple boxes) after you deploy the graphic, it sounds like those elements are not imported into the system and deployed properly.
Once this happens, your graphics are broken and cannot be repaired. You need to import them again.
Something has gone wrong in your upgrade. You should review the upgrade procedure that you used and see if you can identify where you went wrong. Depending on your errors, you may need to start the upgrade again.