S7-200 as Slave with ABB CI854 Comm. Module was not communicating.
Sir,we are facing problem while communicating ABB 800 XA PLC with S7 200 PLC as Slave device(EM 277).
S7-200 as Slave with ABB CI854 Comm. Module was not communicating.
Please help me out to solve this problem.
Answers
Is that GSD File is not matching?? or the Slave address itself not detecting?
Similar problem faced for communication with S7-400 PLC of siemens.
As ABB side GSD installed and configuration done similarly Siemens side also done but not communicated. Then installed back version file in siemens library and used that.
In siemens system only we installed previous version hardware file but in ABB used current GSD. Now it it sommunicating.
So please check GSD files and in both side and if required change in S7-200 library and try once. Sometimes compatibility in version may cause problem. Please don this once if slave address is matched.