DigiVis in connection to AC 800M controller via Freelance PLC connect as OPC client?
Did someone succesfully connected AC 800M controller to DigiVis?
Do you have any selfmade faceplates for DigiVis available? Willing to share here?
Or did anybody successfully connected AC 800M HI (SIL3) controller to DigiVis?
Voted best answer
Answers
Yes, we had connected AC800M cotroller to digivis via OPC in test setup,it is possible to read/write values.
Selfmade faceplates of ? you are looking for faceplate of AC800M TAGS as it is in PPA ?
About AC800M HI (SIL3) controller to DigiVis connection, no idea!!! interested to know....
Regarding connection to AC800M controller to DigiVis, We did cross connection between AC 800M (don't remember PM 8xx version) to CBF/DigiVis through OPC & AC 800F to CBM through freelance connect via OPC in test setup for test purpose.
It is possible to connect OPC Server of AC800M controller to Digivis OPC Client, but there are some known limitations when creating tagtypes & faceplates for the same. I can share the details offline.