How to config HORN
Hello,
I try to config the Horn for the Controlroom. I take a Horn-FBS for the Field-Horn, when I set the Input TRUE the horn will be activated. In DigiVis I can see that the Controlroom-horn will be active, but I cannot hear a sound. It works fine With normal Errormessages Prio 1-4 and Systemmessages S1-S3, but with the Systemprio-Message "0" from the Horn-FBS comes no sound. Where can I config the Soundfile for the Systemmessages Prio 0?
Answers
Greetings,
Under OS1 proterties you can configure alarm sounds and message groups:
According to help file, Horn is only activated via With normal Errormessages Prio 1-4 and Systemmessages S1-S3:
Hope this helps you.
Hi,
horn FB tag you need to map at field horn tab in digivis parameterization. And I suggest tick mark all check boxes for all system/priority messages and try.
btw didn't get you on [Systemprio-Message "0"] there is no S0 or priority 0 messages
Thanks for help.
When I use the Horn-FBS and the set it TRUE with a Bit the Field-Horn would start.
In Digivis I can see that the controlroom-horn starts, but I cant hear anything, because the message from the Horn-FBS has Prio 0 and I could not choose the soundfile for this Prio.
Hello,
To be frank, I am not aware of this Horn block.
But, can't you just operate a DO(digital output) by a simple command to it.
This will simply energise your corresponding relay to that DO.
Correct me, if I have understood the question wrongly !!
Add new comment