Digvis OPC Configuration
Dear Sir,
Can you Provide Example for Configuring to Fetch 2 OPC Server data to Digvis.
Can you Provide the Contact Details to reach you Out .
My Contact +974-70455994
Answers
1.Configure two DGS(Gateway Station) in Freelance tree structure and create two DGS in HArdware structure. If you have two controller then each DGS can be used to fetch OPC data from individual controller, else both DGS will fetch data from one controller.
2. Assign the resource names created in Freelance tree structure to the DGS created in hardware structure.
by Govindaraj
Is your configuration AC500 PLC with Digivis 500 or Freelance system?
by hprashanna Rank: 2546 on 12/24/2017 9:34:36 PM | Like (0) | Report
My configuration 1.AC500 PLC with DIgvis 500 ( that is working fine. 2 In the same Digvis I need to add the other OPC ( kepware which convert Bacnet/ip to OPC server) need to in same digvis. URGENT PLEASE Support.