PM554-T-ETH - Invalid configuration data isuse
Hi,
I'm trying do some tests with PM554-T-ETH PLC but even I try to use Multi online change tool or download new program from CoDeSys I always get the same E3 errors:
- Invalid configuration data
- Invalid configuration of Onboard I/O module
- Invalid configuration
- Project contains invalid configuration data
It seems that the PLC can't get/contain any configuration from PS501. For example, I configured COM1 to Modbus, but in CoDeSys PLC Browser command "com settings" shows: Protocol - Online and Config - not avail.
Please, ask for more information if needed.
Thank you for suport
Answers
Greetings,
Could you please check your firmware version in PS501(Control Builder Plus) and CPU are appropriate?
Also one point with Com port, if you configure as Modbus Master you have to set address to 0, if you set another address CPU does not recognize it.
Hope it helps.