I tried to communicate pm573eth and acs550 and got the following error code.....: 700D,3003.....please any sugges..
i used ACS_COM_MOD_RTU,ACS_DRIVES_CTRL_STANDARD blocks,communication via com1(in plc),emmbeded modbus RTU (in acs550), used terminating ressistor in both the ends...
Voted best answer
Hi,
Have you ever activated the Integrated resistors (pull-up, pull-down)?
Please see below picture:
Also 700DHEX means reading register error? May it be caused to read unaccessible register address? Could you please share with us your reding address, baud rates and other modbus settings(both plc and driver side)?
Answers
i ve cleared the error :700d and 3003 by changing the server to client in plc,but now one more error appear (i.e)=2013 timeout error.....what time should i set?
problem solved.....changed the settings in the drive.....as required ....communication established.