AC800M OPC server with AC800M Controller
Is it possible to use AC800M Controller + AC800 OPC server separately with thrid party SCADA /HMI system directly without using 800xA
Voted best answer
Hello,
If you want to use AC800M + AC800M OPC for thirdparty SCADA/HMI?
Yes, You can achieve in 2 ways.
1. For DCS/SCADA applications You can use 800M with Compact control builder+Compact OPC server to browse the OPC values as OPC Data item without using DCOM settings.
2.You can modbus TCP/IP module CI867 to integrate with SCADA, suppose if you don't want to use 800M OPC for browsing the values.
Suppose if you are using PM865 controller for SIL applications then use the following.
1.Standalone control builder safe for making logics & to integrate into 3rdparty DCS/SCADA applications
Answers
Hello,
Yes its possible to integrage the 800M & OPC with 3rd party HMI/SCADA
Please refer the attached manual refer the page2
Add new comment