Alarm Response Navigation
Answers
Hello,
Alarm response navigation feature is supported only in 800xA 5.1 FP release only.
If you want to create this feature you have to do the following:
1.Create the aspect "Alarm response settings" under the respective workplace from
Workplace Structure > Web System Workplace > Plant Explorer Workplace/Operator workplace.
2.Enable the Alarm response navigation check box.
3.Here You have to select the mode, object path, category,
ex: If you select the mode as "path & category" then no need to select the object path then you select the aspect category/name as "graphic display PG2" it acts as global settings for that workpalce to navigate from the alarms to the graphic display & if you want, on navigating it should open the faceplate also means then in 2nd line of the mode tab you select the "references" & select the "faceplate PG2" from the aspect category/name tab.
4.To get the effect of the settings then Close the opertor workplace & re-open again
Please refer the snap.
Note:Mode is "Disabled" is selected means navigation is not done for this mode
Thanks for the answer. I have implemented these settings but I am still facing 01 problem. If you look on the attached picture you will find that alarm response option created in menu is still not active. How I will activate it?
I want to cofigure the setting of alarm response so that face plate, trend and the graphics where this tag is located should be opened when operator click on to alarm response icon in tool bar of process alarm list. please guide me settings for that. Alarm response is active now in context menu but not working like I want it to be.
Hello,
You please perform the following in the alam response settings for the respective workpalces:
1.enable alarm response navigation
2.Select the "references" in the mode & select the aspect category/name as "graphic display PG2"
3.select the "path & category" in the mode & select the aspect category/name as "Faceplate PG2"
4.Make other modes as "disabled"
refer the image:
Now this should work
Add new comment