PID in fieldbus instruments: AC800F
Hello,
someone has exprience with PID controllers that come in Fieldbus Instruments,
in a few days I need to configure some valves Fisher (field bus foundation) using control builder F.
especifically i have doubts about how to gain access to PID parameters and values in control builder F.
also if someone has one application where configure one PID in the instrument?
Thanks in advance.
Voted best answer
Dear csanchez
Check link below where you can find if that device was integrated and tested before, in short verify compatibility of device type with freelance version you are going to integrate device with, if not contact at dic@in.abb.com,
Also when you upload .cff file of that device type you can find AI/AO/PID blocks which you can configure in CBF FF_FBAPP and download to device. Also those H1 variables you can map to IEC613113 to use in freelance logic and to display in DigiVis.
reply back if you find any difficulties
Add new comment