How to disable permanently orange color crossmark on alarm bands when any AE collector services fail
Hi,
Is there any way to permanently disable the orange color crossmark on alarm bands, (want to hide that feature as it's not required by our customer).
They want only system alrm when any alarm event collector services are down.
Suggest me any work around to fix this issue
Voted best answer
Proper indication of malfunction has been and still is a cornerstone of a professional control system such as System 800xA.
Without the orange border indication, the total loss of an entire Event Collector group becomes significantly reduced.
[Library Structure] -> Alarm Collection Definitions -> OPC AE server of choice -> Alarm Collection Definition [Config View] - clear the Significant Alarm Source (gives visual notification) check box. Restart concerned Event Collector service groups.