I tried to add a redundant connecivity service, but the server services ar not coming up. 800xA 5.0 SP2 REVD
The redundant connectivity server (CS2) was out of service. I disconnected the failed redundant connectivity server(CS2) from configuration wizard of Aspect server 1 (AS1). Installed a new 800xA5.0 SP2 REV D system in a new machine as a redunant connectivity server(CS2)
While adding the redundant server through the configuration Wizard, it is getting added and all the services are created in service structure, but showing the service status undefined. Not able to restart or stop the services.
1. RNRP was found okay.
2. host files are same as other servers.
3. All the installed sofware vesrion are same as other servers.
Please refer the attached screen shots for reference
Voted best answer
Try rerunning ”system software user settings” in the config wizard.
Ensure no old / obsolete OperateITTemp/Data folders are blocking new ones (if needed take ownership & erase them).
Try ”Connect node” from Node Administration structure (the button in the Node Definition)
Answers
If you have joined CS2, please try rejoining as redudndant connectivity Server.
Stop server and remove from the 800xA system. Make sure Domain rejoining for CS2 was perfactly done.
After remove from 800xA restart the CS2 node and after machine is up and running then re do system configuration setting through configuration wizard.
Now join it again as redundant connectivity server.
Add new comment