What are the benifits of having Faceplate in 800xA with AC450 controller?
What are the benifits of having Faceplate in 800xA with AC450 controller? If choose not to go with as per the signal count of AC450 system. Wheather I will be in loss?
Voted best answer
Hi
Faceplate are generally given to monitor and control the data and alarm.
you can avoid system default faceplates when
1.If Tag license count is less than signal count
2.can avoid faceplates for Feedback Digital inputs
3.Seperate faceplates for AO may not be required in a close loop
4.Serial communication tags may not require
5.If customised loops are configured then we can elimate the faceplates for each signal.
6.Interlock signals may also not require