HART Aspect Objects 800xA
System: 800xA 5.1
I would like to make on-line operations with HART transmitters from Engineering workplace - parameterizing, diagnosis etc. through AI815 connected to controller via ModuleBus. Do I need license HART Aspect Objects 800xA for this case?
Thanks.
Answers
AI815 does not support HART interface, you can use AI845\AO845\AO845A and AI895\AO895 each eight channel modules to connect with you HART transmitter.
Dear Sumit,
Please argue why AI815 does not have HART if it is stated in manuals for 5.1?
Thanks
http://www05.abb.com/global/scot/scot354.nsf/veritydisplay/7b48eabe6eae685bc125
796d00346702/$file/3bse020924-510_a_en_s800_i_o_modules_and_termination_units.p
df
Please see page 79.
Dear Eugene,
It was lack of my information, any inconvenience caused regretted. Yes AI815 supports HART communication. Unfortunately I was referring document 3BSE025251R5021 till now for S800 IO HART related issues where there was no info about AI815 in HART Communication section. Find here with screenshot of the pages. Good to get correct document reference from Henrik.
Thanks
Thanks Boris, Sumit, Henrick.
Now we all know that AI815 supports HART :)
How much licensed HART Aspect Objects 800xA do I need to have - as much as HART devices are connected to AI815 analog inputs I will operate or as much as I have displayed faceplates for HART device in one time?
Thanks
Hi Eugene,
You need one "Hart Device Aspect Object" per HART device. You can buy them in packages of 100, 1000, 10000. Every HART aspect object accessed with DTM counts as one.
Br
H
Hello,
One Hart Device Aspect Object per HART device is required, i.e one license per object. Every HART Aspect Object accessed with DTM counts as one. As a general rule, the number of licenses you would require is equal to the number of AI signals that you have.
Best Regards
Monisha
Gents, thanks a lot!
It now clear. One more question about HART managment - engineer and operator will see on-line information from device in faceplate in form as it shown in PACTWare window, for example?