HART CCB800
I would like to use AI 815 analog input with Hart functionality together with CCB800
Is it possible to read out those Hart registers from the module in to the program.
What i heard it's not possible with CCB800, is it so?
If it so, is there any work around?
Best Regárds
Jörgen Malmström
Voted best answer
From the compact products suite it is not possible to use the Hart (or any Device Management) features. From CCB it is not possible to read the Hart values of S800 IO (you can only configure the AI815 module to talk HART), these are tunneled through the controller to the HART OPC Server in 800xA (HMI System).
If you are using compact HMI then you dont have this HART OPC server hence no device management functionality available.
If you would want to have HART then you would need to upgrade to a 800xA System, HW wise no changes are needed, but SW and licenses wise yes.