I am programming of ABB AC800(PM861A) controller.We have a WEG drive type CFW11 and I have to connect drive to controller via profibus.I have not this till now.How can I configure this connection.Has somebody a sample to help me.
Thanks a lot.
Answers
Hi,
you can download already tested device object type for WEG drive type CFW11 from abb solutions bank, Provided you have access to abb solutions bank.
@ http://solutionsbank.abb.com/SLH/intr...?
Hello,
You have to do the following.
1.Create the Hardware tree with CI854
2.Establish the Communication with drive using DP-PA gateway.
3.Check in live list of controller using web browser before giving any address & extracting any Object type.
4.Then extract & install the Object type through the device library wizard.
(You have to get this object type from ABB Solution bank & enusre its approved by 800xA)
5.Insert the Hardware lib of the perticuler object type.
6.Enable the tool routing.(Ensure max no. of connections per controller are 50 please don't change this setting recommended)
Now you can declare variables & assign it.