Upload two subnets in one OPC server IEC61850
Hi,
I have a system with 4x IEC61850 OPC servers.
On the 4th server im trying to upload two subnets, WA4 and WA5.
Both subnets look OK in CET. But when im uploading it to the functional structure only WA4 appears.
The SCD file is built in IET600. SCD file is attached.
How am i supposed to upload two subnets in one OPC? What is the right workflow?
WA4 include AA1 substation
WA5 incluve RT17 substation
Attached are screen dumps from the system.
Answers
Hey Towik,
The problem with the IEC61850 uploader is that it only imports the first substation. To allow the import of multiple substations I recommend to follow these steps:
1. In IET600 create the project with multiple substations
2. Export the SCD file from the project and import into CET
3. Split the IET600 project into two projects, one for each substation
4. Export these two SCD files and import them into 800xA
Alternatively edit the SCD file and remove the first substation. Then re-import the second subnetwork. This will add the second substation to the functional structure.
I've had a look at the SCD file, for me to understand a bit better. For your system there are two physical servers or virtual machines that are redundant? For each of the servers you have 4 OPC server instances as follows?
Instance 1: WA1
Instance 2: WA2
Instance 3: WA3
Instance 4: WA4 & WA5
Best Regards
Christo