Advant MOD300, Diagnostic errors,
Hello!
After upgrading Advant MOD300 Engineering Station from 3.3 to 3.7 we faced with the fallowing warnings in alarm and event list:
PLC: ERR 0 ON INPUT FROM SEG FOR ANA CHAN 126
and
RG: ERROR DELETING FILE
There is MODBUS connection beetween PLC and Modicon via Modbus, but it was no changes in port settings or requests. This type messages appear for all request on the port.
I finded this warnings in 3BUR000261_D_en_Advant_OCS_with_MOD_300_Software__Diagnostic_Error_Messages_Tec
hnical_Reference
Module RSCOPYDI Task RG***LID
FIX = NO_FIXED_ERR, AP = RG+RS_DELF_ERR
AP1 = FMS status, AP2 = File Type (ASCII/BINARY)
TEXT: RG: ERROR DELETING FILE
CAUSE: Error deleting corrupted Schedule Directory file.
EFFECT: Unable to restore corrupted directory.
ACTION: Depends on AP1.
but it take me more clarifying: which file i must delete? What means this warning for Modbus communication?
Answers
Hi , Did you install 3.7 SP1? , try it and to see if the message still continue , another question , Does the system come from advant technolgy before 3.3 ?
Regards
Source: Advabuid for Mod 300
Hi ,how often is the message showed ?
Another information could be useful for other things also :
if you installed until 3.7 you could verify the following information beside of I mentioned above , 3.7 SP1 fixes some problems regarding to PLC and others issues , also it has others Patches to fix something regarding to 3.1 SP1 , here I show you some issues fixed with some patches 3.7 ( no SP1 ) , but it means that 3.7 SP1 fixes them before is higher
Please read it :
There have been four system software patches created for AdvaBuild 3.7: ABBPSSN_146108, ABB-PSSN_146111, ABB-PSSN_146112, and this patch, ABBPSSN_146114. ABB-PSSN_146108 (AdvaBuild 3.7 P2) to correct Power Supply and Fan Status indication: If you have previously installed this patch it must be removed before installing ABB-PSSN_146114. If you have not installed ABB-PSSN_146108, there is no need to install it because the correction is included in ABB-PSSN_146114.
Regsrds
Source: Advabuild
Add new comment