CPU & I/O module warning
Hi,
My system has some warning.
- CPU:
+ HWState: 16#00000002 Warning
+ ErrorsAndWarnings: 16#68020000 No Time sync, RPA, RPB
- I/O module:
+ HWState: 16#00000002 Warning
+ ErrorsAndWarnings: 16#40020000 Warning
Could you help me to fix it?
Thanks.
Voted best answer
Hi,
Wire the AC800M power supply status inputs SA , SB to 24V.
Answers
CPU warning:
I/O warning:
Hi,
It seems there is some problem in time synchronization setting and Faliure of the redundant power supply A & B on the primary CPU.
see the attcahed controller setting .
refer the below doc for more information on Time synchronization .
"3BSE034463-510_en_System_800xA_5.1_Network_Configuration "
Regards
Ravi kant Gupta
Here's my CPU setting
The Power Supply status indication not wired from power supply units to controller, therefore AC800M will always report RPA/RPB alarms.
if alarms are required to be cleared, then the status wiring needs to be installed.
Hi,
Check for the Controller settings for Time synchronisation. Disable it if not required.
Check whether the end connectors have been made for the controller optical extension.
Also check for the connections for fibre optic connectors for the cluster modules and the end cap in the last cluster module.
by Linkinx64 Rank: 69 on 3/2/2013 11:05:01 PM | Like (0) | Report
Hi,
what are CNCP settings in the AC 800M PM856 hardware?
by tuanPASCO Rank: 218 on 3/2/2013 11:19:07 PM | Like (0) | Report
I've uploaded screen-shot for CPU setting in last answer.
Add new comment