Access of third party opc server tags in system800xA
hello Freinds
I am automation engineer and I have done a lot of project with ABB system 800xA.In my current project (system 800xA ver.5.1)I have installed a third party opc server to our connectivity server and then I can see the varaibles on third party system via opc,but I don't know,how can I access in this values in my project in control builder and graphic Builder.Please help me.
Thanks
Voted best answer
Hello,
if you are going with PLC connect then follow this
1.You have to go for the ABB PLC Connect which you can install separately or you combine with default AC800M connect package which is having inbuilt drivers(Modbus TCP/IP, Modbus RTU,COMLI,Sattbus TCP Master) then you can get all data directly then you can perform the graphics building for those values.
You have to create separate Generic control network. If want to use in control builder then you have to go for generic properties aspect
Please refer the attached doc.
2. if you are doing generic OPC then you have to use the property trasnfer definition to use the variable in CBM.
refer the doc attached