RTA Board adding error
I am trying to add RTA board (Adavant Master) in the exixting Xa system,
the bellow error is coming, any body knows the solution to fix this without reinstalling the xA.
XA revesion is 5.1 Rev A
"E_AFW_AOM_OBJECT_NOT_FOUND(0x8abb090a) Object not found in the object manager".
Voted best answer
Please check that the following RTA services still are listed in the Service Structure:
- AdvMbStatusList
- MasterBus RTA Management
- MasterBus NodeStatus Server
- MasterBus TTD Configuration Server
- Masterbus TTD Data Server
When adding an RTA, service groups for the above listed services become created. If the parent object is missing, the wizard can not add any child.
I've seen this error happen when the TTD Data and TTD Configuration services had been removed from the Service Structure (site was not using TTD and had deleted these services)
These services can be restored by double clicking the corresponding .SDD file in this folder: c:\Program Files\ABB Industrial IT\Operate IT\AC 400 Connect\sdd
AdvMbNodeStatusBase.sdd
AdvMbRTABase.sdd
AdvMbStatusListBase.sdd
AdvMbTtdCfgSrvBase.sdd
AdvMbTtdDataSrvBase.sdd
/Stefan
Answers
Have u select RTA board(PU515 or PU410) during installation of AC400/Safeguard Connect?
if not goto Control panel-> Add or remove programs->right click on AC400/Safeguard Connect->select change features
Add RTA and restart system once.
While it is recommended to disable Data Execution Prevention on your Windows computer.
Source: PU410
Add new comment