I want to use AC800M-HI(PM865) in a small safety system,which licenses do i need? if licenses F-160(high Integrity and Process Control) and F030(PM865 license) are enough or B010(800xA base system) and G010(engineering workplace) are needed too?
"800xA base system" is expensive for small systems.
Voted best answer
F160 is required if you are going to run both DCS and safety applications in the same controller. otherwise you need to consider this license. F030 is the controller license and is must with system 800xA. The base system include one Operator and engineering workplace license and you shall order additional workplace license accordingly. With regard to pricing, you may please note that we will be launching standalone safety soon, so that one need not buy system 800xA license. One can buy engineering ie control builder safe license only. Also, it will be possible to use Compact HMI or any third party HMI using MODBUS or OPC.