5.1 Rev D FP4 Event storage, maximum no of event can be stored in reduntant ASCS..?Kin
Hello,
1.What will be the maximum event and alarm cabe stored in reduntant ASCS configured system..? I am not getting events older than 5 days. this is the one of common complains from customers..!
2.What is the maximum File size , file count and message size can be configured in Event stoarge Special configuration(for Simple condition event & Process Condition events)..?
3.And how it effect the system load..?
Answers
As not getting events more then five days. It looks like event generation rate is more and same will be consuming defult storage (10000). This also depends on what you have checked under event logging. This works as FIFO(first in firts out).
If require you can increase it from service structure.
Alarm Manager service group >> service group definition >> Special configuration tab >> Alarm storage >> edit .....
Note: After change It requires a restart of Alarm manager Services to be effective for system.
Not adviible in running production enviurment.
Please contact ABB supportline for more info.
Add new comment