Export Alarm-List to excel
I know with the function copy/paste I can copy an alarm list to an excel-file. But an alarm list is limited to 500 events. Now I'd like to export more than 500 alarms, and I don’t want to use to PageDown... copy.. PageDown... copy
Is there another way to export Alarm event to excel (Bulk Data Manager?)
Voted best answer
You can use Copy/Paste option only to copy the visible alarms which is 500 Max at a time.
For your requirement, as Ronny Suggests you can use the Data Direct which is one of the Data Access Tools provided by IM. Refer to Section 2-3 in
System 800xA Information Management Data Access and Reports Manual (3BUF001094-5xx C) for more information on this.
Workflow would be simmilar to Bulk Data Manager. Once you install the product, it can be activated by clicking on "AE" icon that you get in Excel Sheet Plugins.
Answers
Hello,
the easiest method is with Data Direct. Use the AE button.
If you have an IM you can also use SQL language, and the alarm and event list can be extended up to 12 million events.
/Ronny