SFC Viewer Problem
Greetings,
I've problem with SFC Viewer. According to attached screenshots:
For Control Builder M, under SM1 Single Control Module, I have a SFC codes.
For Engineering Workplace, under elated single control module, I've created the SFC Viewer Aspect.
When I double click the that aspect, it shows me nothing.
My system is 800xA v5.1 FP4.
Dou you have any idea about it?
Voted best answer
Hi,
To view the SFC Code in Control Structure, SFC Viewer Aspect needs to be activated using control builder. For this Go to respective Control Module[SM1 in your case] and then Tools->SFC Viewer Aspect. Check it.
I hope it helps.
Regards,
Ashish Sharma
Answers
i suspect u didnt completed the SFC Uploader.
Please follow below mentioned steps:
(Please make sure that :
a). In "Control Builder" ---> Control Application---> Select your "SM1" & edit it from
where you created the SFC.
b). Select the "Code Block" (avaialble at left side) of SFC &
Right Click on it &
make sure that
"SFC Viewer Aspect" & "Step Elapsed Time" are checked.)
After this ,
1). Open Plant Explorer --> Select Control Structure --> Select your Control Application (under which application SFC is been created by you).
2). Select " SFC Uploader " aspect (available at left side).
3). In " SFC Uploader " aspect --> Mention the value for "Display Tag Separator" (e.g. 1 or 2 or 3...)
4). Press the "UPLOAD" button.
5). Wait for few minutes & check the SFC Viewer aspect.
Hope it will resolves your issues.
Add new comment