How do I in the fastest way connect an ABB Drive to AC800M?
Answers
Source: JMS Automation and Drives
Hi
There is multiple ways that you can connect the ABB Drive to AC800M
1. Profibus Via CI854A on Profibus
2. F.O Network CI858 thorugh NDBU or direct connection
3. Modbus via CI853 through STP wire
and most simplist is to do the hardwire.
Source: ABB Drive Communicatrion
Ac800M ----FO---->ACS800(RDCO) DDCS Communication
Ac800M -----Modulebus
ACS800 -----98.02 Advant, 98.07 ABB Drives, 70.01-Node Address(AC800M Modulebus)
70.04 ring/star
90 group Ref from AC800M
92 group Status/Actual Variables feedback to Ac800M
Connect as many drive use NDBU.
Follow AC800M Firmware Manual
Greetings
the fast way is using the module bus , but it need addition card in the drive to do so
also you can do that by the old way (the hard wires) , but your had to take the limited data transfere between the drive and the controller
regards