Add a new subnet to an existing IEC 61850 OPC Server
Hi,
I have four opc servers in opration with one subnet under each, wa1 - wa4 (switchgear).
I want to add a new subnet wa5 under server four. I have imorted wa5.scd file into the CET-tool, looks good, online diagnostics ok, Update&Reload ok.
The problem is that IEC61850 gets stack and not running properly, no control structure and no functional structure is created.
An error message exists in the log file: "IEC61850ocsPostProc component does not exist".
Anyone?
Best Regards
Jonte
Answers
In CET you might be able to add the subnetwork but you cant do the same in control structure.
Better option is to delete the least critical SCD file from CET & 800xA & recreate it by including the new elements that needs to be included.