Is it possible to configure alarm shelving on a per tag/functional area basis? I couldn't find alot of information in the 800xA configuration manual regarding this feature.
I would anticipate you could add an aspect to the tag that takes precedent over the default configuration...but that didnt seem to work. I tried it at the tag level.
It would be nice to be able to group alarms into "alarms that don't require double authenticate", "alarms that can be shelved for 1hr", "alarms that cannot be shelved", etc.
Answers
Shelving an alarm need permission - you can throttle who can shelve, what object and from what node.
Apart from shelving, you can also use alarm hiding to remove an alarm. Starting with v6 you can also have alarms hidden retroactively (after they go active).