AI830 on 800xA/AC800M - Temperature Offset
Hello,
we have a problem with the right indication of a Pt100 temperatur signal, which is acquired by AI830 module.
S800/AI830 (TU810) module is connected via Profibus to the AC800M controller.
External wiring is in accordance with data sheet, was checked and is ok.
Unfortunately we get a temperature offset of 30..35 °C.
Configuration is attached.
Any ideas, what could be wrong? Regards HolgerVoted best answer
Hi,
I think the reason is the difference between channel signal range (-200...850) and the scaling (-100...600).
If that is Pt100 measurement, both should be equal: first select channel signal and then write the same scaling for the variable. It dorsn't matter what is written in your sensor - select channel range closer to it for better accuracy.
Answers
Seems scaling issue.
Please change scale settings and download onceagain.
Add new comment