We would like to use a AC800M with a CI869 as slave on AF100 bus connected using FIX SCADA.
We would like to use a AC800M with a CI869 as slave on AF100 bus connected using FIX SCADA.
On FIX SCADA there is a OPC server. Will there be problem connecting the AC800M node through OPC?
Today there is a AC70, but we would like a more future-oriented alternative.
On FIX SCADA there is a OPC server. Will there be problem connecting the AC800M node through OPC?
Today there is a AC70, but we would like a more future-oriented alternative.
Answers
If you use an AC800M you shall not use AF100 but Ethernet TCP/IP and install AC800M OPC in the FIX SCADA system. To connect AC800M using CI869 (AF100) to FIX does not work very well.
In this case, use Compact Control Builder AC800M which contains Control Builder and OPC Server.
In this case, use Compact Control Builder AC800M which contains Control Builder and OPC Server.
by Gero@ABB Rank: 534 on 10/5/2011 3:30:31 AM | Like (0) | Report