Is there any suitable IED for MicroSCADA availlable to generate a *.scd-file or is there a need to put an additional RTU for the interface ?
Answers
If the IED has the feature of iec61850, the CI868 can directly communicate with it via MMS or goose messaging. You may create an scd file in PCM600 and import it into CI868 in CBM. Following manual provides a good workflow for both MMS and goose: 9ARD171384-510_B_en_System_800xA_IEC_61850_5.1_Engineering_Workflow
MicroSCADA supports only MMS for IEC61850,AC800M supports both MMS(Selected LN) and GOOSE through CI868 card.You can use IET600 to create SCD file for MicroSCADA and 800xA/AC800M.All supported IEC61850 IED can communicate with MicroSCADA or AC800M.