Solution of 800xA with Device Manager but using Wirless Hart for connection to the Instruments?
Someone have reference about a solution of 800xA with Device Manager but using Wirless Hart for direct connection to the Hart Instruments instead Hart Multiplexers, how is indicated indicated in the file attached
I need an Architecture, Drawing or Diagram where this configuration is showed someone can tell me where I can find it?
I need some project reference with this solution someone can tell me where I can find it?
Voted best answer
Hi Topology is next:
For more information check document:
System 800xA Device Management
PROFIBUS and HART
Configuration
System Version 5.1
docuemnt number 3BDD011934-510 C
Answers
DTM communication with WirelssHART is possible and it is managed released functionality i.e. you need to talk to ABB support for getting DTMs for Wireless HART (P&F Gateway DTM).
hello Eurit,
the references given below are perfect. Incase you have further questions specific to the project, please get back to me at neil.shah@de.abb.com.
I am the product manager for above solution in 800xA.
regards,
Neil Shah
Product Manager - Fieldbus
ABB Automation GmbH
PACT - System 800xA
Wallstadter Strasse 59,
68526, Ladenburg, Germany
Phone: +49 620 371 2096
Mobile: +49 171 554 2526
email: neil.shah@de.abb.com