Dynamic alarm list configuration
Is it possible to hide all alarms of an alarmclass, depending on an controller variable or similar.
That means a dynamic alarm list configuration.
I am using SV5.1FP4
Answers
Hi
Following would be my suggestion:
- Create a new Alarm and Event List Configuration in the Library Structure
- Open the Configuration in Config View
- Filter Tab - Area Tab - Fill the Class details
- Filter Tab - Attribute Filter - Fill the expression on Attributes required.
- Apply and use this configuration in your alarm list.
This may help you.
Best Regards
Sunny Khatri
Use "3BDS011222-510_D_en_System_800xA_5.1_Configuration" document for configure alarm Hiding Rule.
Hope This will help you
Alarm hiding will prevent selected alarms from appearing. But strangely it doesnt actually hide an alarm after it has been generated.
You can use Alarm Shelving to temporarily remove alarms from lists.
Add new comment