CBM Professional - Tasks Times
Hello folks,
I'm trying to figure out the meaning of every column from Task Overview but, I'm in doubt about "actual interval time" and could not find any documentation.
For example, I have a task where "interval time" is set to 250ms and I understand that when there are collisions "actual interval time" can increase as that task is waiting a high priority one to finish. However, sometimes when I open Task Overview "actual interval time" is below 250ms (i.e. 200ms).
I'd like to undestand real "actual interval time" meaning and how it can be shorter than set "interval time".
Cheers!
Answers
Hello,
I hope you might be aware that, load balancing (Enable Overload compesation) in controller setting (if enabled) will increase the interval time of tasks (except time critical tasks) to limit the cyclic load to 70%.
The interval time will be decreased back if the load falls below 70% again. This will not bring down the interval time to less than the original defined interval.
Is it possible to share the task overview and task analysis screen shots?
Source: 3BSE035980-511