800xa v5.0 faceplate
Dear stefan
we are using ac450 and 800xa 5.0 ,in our plant we have sequence and manual mode for motor faceplate.
sequence mode is used for group start/stop and manual mode is for individual start/stop
here we are not using auto button.
i just want to control the motor faceplate changing from manual mode to sequence automatically , after some time or from Controller program bits .when the motor is in manual mode.
with regards
veko
Answers
Hi,
Normally trigger from Manual -> to Sequence will be triggered in 2 ways
1. There should be as logic to trigger Sequence bit in MOTCON PC element , -- that needs to be ditructed.
2. Opetator has to operate the sequence button from the face plate to trigger the sequence mode. you need to disable that button. you can do this for a individual motor or for all motors based on your requirement.
Add new comment