IEC61850 - OPC server not an 800xA-node
Hi!
Is it possible to communicate with an OPC-server which is not a 800xA-node?
How do I set up this in my OPC DA Connector Service Provider?
Is it by using Remote OPC Node in some way?
BR /asp
Answers
Yes.
You must understand the DCOM-requirements and the two way communication required for this to work. This is not to be taken lightly - its complex any may involve up to four (4) different accounts, some with matching passwords.
Avoid using accounts with administrative permissions - instead enable the permissions needed (remote launch, remote activation outgoing and remote access on the return) in the DCOMCNFG.EXE tool. The OPC DA Connector need to run as the 800xA Service account (which need to be admin in the server it is running on).
Enter the remote node's address or name in the field on the Service Provider definition.