Repeated error while adding ET200M IM 153-2 on CI854
Hi,
I need a urgent help as whenever I am adding ET200M IM153-2 ( MLFB Number 6ES7 153-2BA01-0XB0 ) as slave to CI854 on redundant profibus network inspite of using latest GSD file, following errors get displayed -
1) 16#40000014 - Parameter data fault, backup unit missing, Redundant Mode
2) 16#00030001 - Connection Down
Control Builder version being used is 5.1.
Kindly help.
Answers
What is your Profibus-DP network configuration and what is your AC800M configuration?
What are you using as ET200M slave - Device Object Type or gsd-file imported as hwd?
Also look info here
http://support.automation.siemens.com...
What is your CBM version?
See information from fixed problems in 5.1 RevA:
Hope this help.
Hi EK,
we are using CBM Ver 5.1.1-1 (Build 5.1.1110-5), we are using PM861 along with CI854 master to comunicate IM153-2 as a salve device for taking Siemens IO online. We are using GSD file for ET200 module. we are using CI854 HW Lib2.1-7. We are attaching the details for configuration & errors.
Kindly help us to resolve us the issue.
HiV
you've defined Line Redundancy is enabled for CI854 but you have single CPU, single CI854, single IM153-2. Probably this is the reason as far you have standard single-line, non-redundant communication. Try to change Line Redundancy to disabled.
What are using for ET200M in CBM - Device Object Type or imported hwd-file from gsd-file? If imported - what is importing setiings?
Hi EK
i tried to disabled the Line redundancy & the problem is still same.
I am attaching the details when i imported the GSD file.
Also please advice me how i can import the device object type in CBM.
Please check & revert.
HiV
I don't see nothing special in your settings, it should work. I'm not sure, but probably your gsd-file is prepared for redundant mode only. Find ;Redundancy section in your gsd-file. Parameters in this section are un-commented (there is no ; mark at the beginning). Make all lines commented in ;Redundancy section with ; and import again. Or take gsd-file from link I posted before and import it as new device.
HiV
did you find the decision?
Add new comment