800xA for MOD300 Connectivity Server UseGlobalAck
Dear Users,
I have a Advant MOD300 system with a mixture of
800xA ver. 6.0.2 client and some Advant Station
I have set di "UseGlobalAck" parameters in the Connectivity Server
and now it is possible to ack alarm on the Advant Station side .
Unfortunately I saw that the same "Acknowledge" action made
on the Advant Station side only works on the 800xA alarm list as regard
the acknowledge of the event but doesnt stop the alarm sound.
The only way to do so is by using the silence tool push button on the 800xA workplace.
I wonder if this behaviour of the A/E application ii is "as designed"
or if could be corrected .
Thanks a lot
PB
Answers
Hi , Did you restart the connect nodes after changing the register and follow the instructions to avoid synch problem of the alarms in the 800xA System?
I have read the known problem version 6.0.2 for Mod 300 Connect and it is not mentioned.
Did you verify about send global Ack to Mod 300 register from connect nodes ?
Did you verify in redundant partner register if it is properly configured in connect
nodes?
I think it is well configured according to your comment and from specific manual for Mod 300.
I hope it helps ,
Regards