Function Designer, Generating configuration data fail
I need to write the channels of a DO820 module, which is connected to the CI801 slave in profibus. I use the variables for the CBM that supposedly do not need more configuration, I can host the variables but when trying to write in the CBM I send errors and when I compile it indicates that the system does not know the type of variable that I intend to connect. What am I doing wrong? Thank for your support, regards.
Voted best answer
The problem here is properties configured for DI810 module in CBM and CBM_SignalParameter properties of CBM signals are not matching. This issue can be solved by changing Activate filed to true in Channel Settings of CBM_SignalParameter aspect. This should be done for all digital signals inserted in FuD. Sometimes this issue appears for analog signals also.