DCS800-AC800PEC
Hello,
I was seeing your Answer respect to connection between AC800M and DCS800 (some months ago).
Im trying to do the same with a AC800PEC and CI858 with Compac Control Builder.
I have an error when using ABB Engineered Drive (on Unit Statud Tab says: Channel error, Wrong drive type).
Then I tried using ABB Drive Template (basic) and dont have any errors, but dont see any Drive Status. How should I configurate the parameters on the DCS800 for using this template??
Can you help me please?
Thanks!
Voted best answer
Hello
Please find the attached drive parameter and set it accordingly i am feeling that your drive parameter are not matching.secondly the screen shot which you attach showing you are ablt to communicate with drive.
Try by adding the standard drive first is there any sepcial requirment of the engineering drive ?
If this will not work then let me know but i appricatate also if you attach the screen shot of the status word which are getting status and this will only possible when u connect to th drive and there should't be any red cross in hard ware structure.
Are you ABB Employee if yes then also send query to your support line with all supporitng screen shots i am not sure that if soultion bank can help you :-)
(i am unable to reply in your Question CI858 Firmaware Upgrade for this i reply here)
Source: DCS800 Drive Communication
Answers
Greetings
i hope that the follwoing setting will help
if not what is the error massage you do get
a) Communication Parameter Settings in Drive Side as follows:
Parameter Number Setting
1) 98.02 = 'COM-8/AC800x'
2) 70.01 = '1 ' (Node Number)
3) 70.24 = 10
4) 71.01 = Yes
5) 10.01 = MainCtrlWord
6) 11.03 = SpeedRef2301
7) 50.01 = SpeedMax (Speed Scaling Need to Set)
Data From AC800M to DCS800.
8) 90.01 = 701 (Main Control Word)
9) 90.02 = 2301 (Speed Ref)
Data From DCS800 to AC800M.
10) 92.01 = 801 (Main Status Word)
11) 92.02 = 104 (Speed Act)
12) 92.03 = 108 (Motor Torque %)
13) 92.04 = 901 (Fault Word1)
b) Settings in AC800M.
'CI858DriveBusHwLib' = Hardware Library need to Insert in the project.
Insert " CI858" in the Hardware Structure, & then Insert "0-Drive Channel',
Insert "1 ABB Engineered Drive".
Settings for CI858 & Drive Channel - keep default values.
Settings For ABB Engineered Drive "Settings TAB' as follows.
1) DataSet10 Config Status = Read/Write
2) DataSet12Config Sattus = Read/Write.
Connect the Hardware signals in the "Connection TAb".
DS11 Channel 1 = Main Status Word.
DS11 Channel 2 = Speed Ref
DS10 Channel 1 = Main Control Word.
DS10 Channel 2 = Speed Act
DS10 Channel 3 = Motor Torque.
DS12 Channel 1 = Fault Word1.
Main Control Word Should be as per following Sequence.
1142 = Drive in Remote & No Emergency Stop.
1143 = Drive Armature Contactor & Field On.
1151 = Drive Run Cmd.
Then Release the Speed Reference.
Speed Scaling in the AC800 M Software (+20,000 = Speed max in r.p.m Forward Dir)
(-20,000 = Speed Max in r.p.m Reverse Dir)
Torque Scaling in the AC800M (100 = 1%)
Hello,
I did as you suggested and have the errors than you can see in the image.
Could it be the CI858s Firmware?
Im working with a DCS800 Demo, is this relevant??
Thanks!