Problem in CompactHMI 6.0 log configuration
Hi,
I am currently facing an issue in the compactHMI log configuration (whihc is used for trends and reports). I am getting a status saying "Uncertain, Engineering Units Exceeded" on the logged value. Also, i am not getting the trends plotted.
Can anyone help me out in fixing the issue...?
Thanks in advance.
Voted best answer
Hi,
If the object dialog is showing engineering units exceeded then you need to check the Range you have set in the signal configuration. If the actual value exceeds the Max limit entered in range tab you get this error.
Answers
Kindly follow the Below points:
In object type structure
1) Check the Log operator action is enable
2)Check the low limit and high limit value