Hi Everyone,
I do need help to restart DataSet Communication without restarting the AC410 controller.
Is onyone has knowledge about the name of task for DataSet Communication?
My plan is to do as follows:
#KIT <taskname>
#ACT <taskname>
Since I dont know the task name I can not go further?
Any help is hihly appriciated.
Bulent Vurgun
bvurgun@aspltd.net
Voted best answer
Answers
I am not so big expert in this area, but have you studied any documents / guides for Advant OCS (do you have any one)? Maybe you can find answer in On-line Builder User’s Guide (3BDS100596R201).
I found also next:
I assume there is possible to see all task names thru command HELP TASK_NAME or any similar way....
Hello Bulent, this is the answer from one of our Support Line guys. Hope it helps
Br
Henrik
Hello Bulent.
The taskname fo DataSet is CXAA000.
Be aware of that you do this at your own risk.
And if you have "holes" in logical file 109 for dataset, the task will
abort immediately when you try to restart it.
It's not allowed to have "holes" in LF109, all records have to be there in consecutive order.
Best Regards Jan-Erik
Supportline
Hi,
As i understand from your question
1. System is up and running
2. Dta set is created but Act in at Data set A=0
based on this assmption.my reply and solution is as follow
In online builder we can enable the act pin but it won't functions unless the 410 system is restarted.
Solution:Since the Act=0 in the existing Data set,change the ident number,Dtaset name, which is not exists in other DS's
Craete a new data set provide the same parameters like name,net,node,ident etc as it was in the modifed DS,please remeber ...while creating all the parameteres as to be set.
Then remove dats from the modified Data set (existing DS).
Now the newly created DS is ready to communicate with other node.
please revert to me if my understanding or assumption is wrong.
Best Regards
Basaraja E