ABB Control Builder F Error
Everytime I open a project in CBF I get a ``FF initialization Error``,
Please change invalid HSE-IPAddress wiht configuration tool. Local Station HSE-IP address:xx.xx.xx.xx(IP address of my machine)
How can I fix this error?
Is it because of this error that I can`t load any of my gateways? I have a working 800F OPC server which is browsing tags but on CBF it shows that I have no connection to load any changed parts on this gateway.?
Any help would be greatly appreciated. Thanks in advance
Regards..
Voted best answer
There must be conflict of IP address and subnet mask configured with FF configuration setup,
Are you using FF ? if not just deactivate FF node and download, If you are using FF then check FI840 IP address and its subnet mask or check LD 800 HSE IP address and subnet mask, or you can use reset option to bring default IP for FI 840 and LD800 HSE.
Please note FI 840 and LD 800 HSE IP addresses should be within freelance control network to communicate.
Add new comment