Acs550 drive speed change
Hi ,
I can start ,stop drive from control builder on profibus network but drive speed is not changing when i give referance.
Please guide which perameter need to check inside drive to resolve this issue.
I am using ppo type 2 to control drive in control builder
Answers
Greetings,
Could you please check parameter 11.03, this parameter defines the setpoint source.
You have to set is 8, which means drive get setpoint through the Communication.
Hope this helps you.
Hi
in addition to what is already correctly indicated by Titus, I usually also use parameter 11.02 -comm - or set to 8 - to define the active external control
Do not forget to define the upper and lower value of the reference in parameter 11.04 and 11.05 and the limits in parameter group 20, rispectively 20.01-20.02 if you use vector control or 20.07-20.08 if you use scalar control.
Hope this help you
in addition to what is already correctly indicated by Titus, I usually also use parameter 11.02 -comm - or set to 8 - to define the active external control
Do not forget to define the upper and lower value of the reference in parameter 11.04 and 11.05 and the limits in parameter group 20, rispectively 20.01-20.02 if you use vector control or 20.07-20.08 if you use scalar control.
Hope this help you